Comm. Problem with T3000 to SLC 500 with Equustek DL6000
Segen
Aug 2009
Warrior,Al.
Our plant is currently going through a DCS change to a Siemens T3000. We have been running F.A.T. at the Siemens location. The problems we are having is our commands from the T3000 to the SLC are not working. Everything from the SLC to the T3000 works fine. Siemens loaded the configuration for the DL6000 and we`ve built an exact replica of our SLC rack with the same program we have in the field. Any ideas on why we can`t receive any I/O from the T3000 but it doesn`t have a problem receiving them from the SLC? It`s going through DH+ 3-wire blue hose. Thanks in advance.
Can you post some of the specifics of how the Siemens DCS is configured to read and write the SLC system ?
It might also help if you can post specifics of how your SLC is configured to communicate with the Siemens DCS.
If this were my system I'd be going after the serial link with a protocol analyzer.
I am currently back at the plant and not at the test site, but I`m pretty sure the Siemens engineer set the DL6000 up as a modbus slave. Our slc is configured for DH+. Sorry, I don`t have much information. This is our first rodeo with this set up.
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
524
Hi, I am trying to do a very simple program to communicate the PLC with Hyperterminal. I am using a new CP1W-CIF01 Optional Board (RS232) with...
2,557
Looking for anybody that has experience using the older PV550 displays. Have a locked up comm port. Is there any hard factory reset procedure...
1,369
Hello everyone , I have an engineering station with step7 program. I can make the modifications from this PC for 7 PLCs. But now I can not...
1,929
Hi, First post, I am new to this forum. I tried searching with no luck. I am using an Omron PLC - CJ2M CPU32,and I am trying to get it to...
2,398