Problems with Boolean or DINT array and OPC
hardaysknight
Dec 2015
Southeast USA
117
The software: RSLogix5000 + Graphworx32 by Iconics + Iconics Unified Data Browser + Applicom OPC Server
I need to have my HMI software (Graphworx) flash a square whenever a bit from an array latches on in RSLogix 5000. The trouble is I can either use a boolean array (which means I have to use a bunch of unlatch bits), or a DINT. I want to use a DINT, but I'm only able to see the whole DINT in OPC and not individual bits from the array. I'd prefer to be able to use something like a MOV bit to reset the whole array when the machines pumps turn off.
I really hope I made sense.
You have to add the bit level yourself.
See example below.
x= {{RSLinx OPC Server\[PLC080_NBT]Base_C.Gen_DINT[0].1}}
RSLinx OPC Server will be your applicom OPC.
PLC080_NBT is the PLC name.
Base_C.Gen_Dint[0] is the PLC tag
Hope this helps.
Cheers
Mark
See example below.
Hope this helps.
Cheers
Mark
I tried that earlier but it still did not work. So far I'm just using a DINT[16] and used 16 individual DINTs instead of using a single array. I'm using a FLL to reset the entire DINT[16] array.
OK.
This should work.
x= bittest({{RSLinx OPC Server\[PLC_080]Alarms_NF_08}},12)
RS Linx OPC Server is the OPC server.
PLC_080 is the PLC name
Alarms_NF_08 is the tag, pointing to bit 12.
I have got this running on a system here and it works. You have to make sure the syntax is correct.
Cheers
Mark
OK.
This should work.
Cheers
Mark
Thanks! I'll give this a try next week.
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
160
Anyone have problems/solutions with Rehosting Studio 5000 to a new computer. Our IT department successfully Rehosted 2 laptops, but the other 2...
145
Hello. I appreciate the insights here and the willingness to share. I've got a lot of Rockwell experience, but my Siemens experience is...
193
Currently a student, so somewhat new to this. But working with an AB 2080-LC50-24QWB, CCW version 21.01.00. CCW will connect okay to the Micro850...
307