Proface GP4301TM to Omron CP1E-N40-DR-A
aravind.r
Jan 2012
bangalore
Dear friends,
It takes a lot of time to load each and every button in this Proface GP4301 -TM screen.Every page takes few minuted to load.Communication cable and settings are fine.But still it takes a lot of time.Some one help me to fix this up.Thanks
check the comm port setting the default is 9600
you should be able to run it at or above 38400
maybe even 115 kb
I assume you are using the PLC to change the screen
Thanks for you reply.
1. I use both "Change screen " switch in HMI as well as PLC to change a screen.
2Switches which I use in the screen are with lamp feature.
3.The baud rate set in the communication settings is 9600.
4. In system area settings in HMI , I enabled only change screen settings (address D008).
Do u find any discrepancies in the above settings?
the 9600 is very slow for the HMI.
it is the default speed for both PLC Comms ports.
this is considered the safe comms speed.
Most of the time you increase the comms speed before you stert programming.
you need to change DIP sw 4 or 5 - cant remember which.
(I am thinking both)
then setup your comms for 19.2 kb (min usual) speed.
you can also setup the two ports for faster speeds.
The HMI will also need to be programmed to same Higher speed
this will bring everything up to speed.
try it at 38200 - even better
but remember to change the PLC Port also.
I think 115 kb is too fast - not sure (cant remember)
Dear Friends, I am in need of (user made) communication cable diagram for Proface GP4301 -TM color HMI to the mitsubishi FX1N...
1,756
Hi all, i have several Proface GT2400 terminals and i need to get the software and interface cables and i have several questions. I am assuming...
166
I have followed the videos & still having issues getting the email out. Does anyone have knowledge or has sent an email notification via gp pro ex?
196
Has anyone found a Proface HMI that is compatible with Schneider M172 PLC?
390
Hi, I received the following project from a customer on a QuickPanel Proface 6" that I need to swap to a Siemens Panel. However, I cannot seem to...
350