program for colour droping

md.abdullah

Member
Join Date
Sep 2011
Location
motihari
Posts
168
Hello Sirs

i have color injection machine which i am programming.
there is one sheet(5 meter ) where i have to drop color. so i have 30 on/off valve in a row for dropping the color on sheet.
i am getting sheet length from encoder.
My problem is how can i write an equation so that for every 10mm i have to on/off the valve.
i hope you understand the problem.if not then
my simple question is there is 30 on/off valve i have to make it 500 times on/off how can i write program in minimum,

i am using rslogix5000 plc.
 
The first thing you need to do is find the number of pulses that would be required to move the sheet 10mm.
The program would then compare this number and activate the valves. You did not mention how long the valves are open. This could be a timed duration or distance from the pulses on the encoder.

Hope this helps,
 
before you go more further

few question you need to answer to yourself,

1.) the speed of the sheet e.g 100mm/sec? 1 meter/sec?etc.
2.) how long you to switch ON and OFF ?
2.) what type of valve you will use? low/medium/high speed switching valve?
3.) what type of source of device output you to use? transistor/relay/SSR?
4.) do you use pressurizer tank/buffer tank for your color raw?
5.) how you distribute the flow for the color equally?
6.) what type injection valve to use to get smooth spray?

Good Luck
 

Similar Topics

my ccw softwer stops working when i add and try to open a ladder program.
Replies
0
Views
14
I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
Replies
0
Views
106
Hi All, As a precaution my company has been collecting copies all the HMI and PLC programs. I have recorded copies of most of our sites...
Replies
0
Views
73
So basically i have 2 queries : 1. I have a program file of S7-300 PLC which i want to migrate in RSLogix500.In short i want to convert my simatic...
Replies
15
Views
279
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
Replies
0
Views
39
Back
Top Bottom