Prosoft Modbus FYI

GregPLC

Member
Join Date
Oct 2002
Location
Milwaukee, WI
Posts
342
If you're using a Prosoft MVI46-MCM (Prosoft's latest card for the SLC chassis), and you're using a 5/04 processor, it needs to be a series "C" processor or greater to work with the Prosoft card.


Trying to save others headaches in the future,


Greg
 
I would assume this is true for all the "enhanced" SLC's, 5/03 and 5/05 as well. Is this because you have to use Block transfers instead of reading and writing to the M files directly?
 