After years of starting up PLC controls as a field engineer, I have taken a position as a plc controls designer. I have been copying past company designs as a template but I don't want to be a lemming into the sea. I'm looking for personal experience on how best to terminate I/O in my cabinets. Presently I use unfused terminal blocks for 24 vdc digital inputs. 24 vdc relay outputs are used to power interposing relays. I use fused terminal blocks for analog I/O (4-20). The analog inputs are sometimes loop powered from my cabinet. The rest are powered by the field device. The field devices are mostly valve actuators (open/close and modulating), blowers and pumps, and water analyzers in municipal water treatment plants. Are fuses necessary on analog I/O? What are the comparisons of triac output vs. relay out in driving interposing relays? What is your experience?
I work 90% in the municipal market, mostly wastewater. The most common "mistake" I see on designs from consulting firms is over specifying. There is no pat answer to your question - to me the essence of good engineering is to apply general principals to specific problems and come up with the best solution for the criteria and constraints of each design.
I'm not sure about water treatment plants, but I know wastewater treatment plants are notoriously prone to lightning and surges. They are also generally maintained by under-qualified or at least under motivated staff.
For example, I find fused terminal blocks for analog I/O are a pain in the rump - blown fuses maybe SHOULD be the first thing checked, but they aren't, and I'm not sure that the PLC doesn't protect the fuse by blowing first! If I have analog signals leaving the building, I use fused terminal blocks with MOVs and make sure they are grounded properly. If the I/O isn't leaving the building I use straight through terminal blocks that have a disconnect switch. That way I can check my loop current without any wiring or jumpers.
I also generally use 24 VDC interposing relays with relay outputs on the PLC, but not for every discrete output. If I'm only operating a pilot light or a starter or other device inside my panel, and the load current is much lower than the output rating, I skip the relay because it is just another potential failure.
I always include a surge suppressor/filter on the incoming 120 VAC power.
I could go on and on about some of the stupid things I've seen specified by consulting engineers spending other people's money, but the main point is: don't blindly follow a "standard". Think your way through every application. Include all components with a necessary function, but don't include any component just because it sounds like a good idea at first, or because "it couldn't hurt" or especially because "that's our standard".
godfrey
Hi, come up with your own standard, you know what works for you and what don't. Keep it basic, use interposing relays on heavy loads, loads in a harsh enviorment, break both legs of solinoids or heavy inductive loads etc.....
Make/Break of contacts that carry a higher DC voltage and the inductive kick of a DC coil will cause big problems for you if they are in close proximity to your PLC or ASB. (Suppress these)
Triac I/O cards are cheaper but they leak voltage, using Triac I/O cards are no problem in relay circuits. Use contact cards where leakage would present a problem or where you will be using more than one source voltage on the card.
Roger
Hello everyone, been awhile since I've posted..... As the title suggests, using Crimson 3.1 software (Red Lion) I cant seem to figure out if its...
1,711
Hi, Just wanted some thoughts on protecting control and instrumentation from welding damage. We had a PLC and drive fail after some welding work...
4,997
Hi Everyone, Yesterday we encountered an issue where I had a 480V 3Ph 2HP Powerflex 525 blow up. Upon further inspection, we noticed that 10...
21
5,993
Hi, I am currently developing a project and need to know if it's possible that once I download to CPU and HMI no one can upload it and re use the...
23
6,821
We have a PV+400 on our floor that has something quite odd going on. The program hasn't been changed in quite a while, at least a couple of...
5,396