PV+7 Modbus/TCP and Ethernet/IP

mcfarlde

Lifetime Supporting Member
Join Date
Mar 2010
Location
Alberta
Posts
13
Hello, Can a PV+7 do both Modbus/TCP via KepServer to some devices at the same time it is doing Ethernet/IP to a PLC?
 
Yes, as long as it's the "Performance" model, not the "Standard" model.

The "Standard"has the performance limits that used to be part of the "Compact" models, that support only one driver and one data source.

The "Standard" units support one native FactoryTalk Linx Enterprise driver, or one KepServer driver, but not both at the same time.
 