Im pretty sure I can but I thought I would ask .....can you put a 1771-SDN next to a 1771-IFE 2 slot adressing ...I know I can't put it next to an 1771-OFE
 
Question 1771 SDN X1

Question 1771 SDN
Im pretty sure I can but I thought I would ask .....can you put a 1771-SDN next to a 1771-IFE 2 slot adressing ...I know I can't put it next to an 1771-OFE
 
I would say you can't do this.

In 2-slot addressing mode, the pair of modules at the same logical address (2 physical slots) would have to be "complementary", i.e. one is inputs only, the other outputs only.

Since the SDN is both In and Out, it will have to have its own unique I/O space, so you can't partner it with any other module.
 