Hello,

I use Wincc Flexible 2005 and an OP73 micro Panel with a Siemens CPU 222.
How can I send from the plc a created screen on the panel?
Example: When M0.0 is "1" then get screennumber 5 on the panel.
I have searching on the manual but can´t find this remote controlled screennumber option.
Who knows?

Greetings,

mulderm
 
For this kind of functionality you need to use Area pointers. In the configuration panel "connections", select the tab area pointers. One of the pointers is to control the screen. With another area pointer the CPU receives the current screen number.

Regards,
 
All you need to do is have an on change event for the bit. Then in that event select the screen number you want to change. You can bring up a screen by number or by name.

WinCC_Flex_Screen.JPG
 
But when M0.0 is going from "1" to "0"?
Then there is also a change-event for the bit.
I want only go to a screennumber when M0.0 is "1".
For the Area-pointer: I have only one option and that is
the PLC Date/Time function.
No other options are available.

mulderm
 
hi
a)Goto the Area Pointer(found under "Connections" setting of WinCC Flex)
b)Switch "ON" Job mailbox and write any address (say MW170) under address column.
c)In Microwin write code such that when ever M0.0 becomes TRUE, the integer 51 is transfered to MW170(use move command) and screen number(which you want to pop up)to MW172

Thats it
 

Similar Topics

My boss has come up with the idea of renting machines and charging on a per use / per hour basis, so I'm looking into it - just getting my feet...
Replies
14
Views
3,994
Morning All, I don't post much but I am trying to help a coworker quote a job and we are coming up pretty much empty handed. You are the best so...
Replies
6
Views
4,438
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
49
Hello, Can anyone recommend an expandible IO module with OPC UA? I've deployed the Emerson RSTIO-OM module and it works great, but it has a...
Replies
0
Views
46
So I'm pretty new around here but I come looking for advice or suggestions to research. Im the plant electrician/SCADA guy for a warer department...
Replies
8
Views
255
Back
Top Bottom