Hi there,
I am doing work for a customer who has a UDT that uses parameters like this:
PLC_REG_TO_SEND.GROUP_15.1234_DINT[1].0
I believe these tags are laid out with the intention that they will be Produced and that other controllers (like mine) will Consume the tags. I believe the PLC_REG_TO_SEND would be like a Consume path? And the Group_15 is a structure/UDT which has members like 1234_DINT, and 1234_REAL, and so on. I have done a bit of Produce/Consume but not much.
However, I am used to doing MSG instructions, where I might be able to poll each GROUP_15.1234_DINT[k] individually, or something like that.
The issue I am having is that when I try to create a UDT which has a member called 1234_DINT of type DINT[10] for example, Studio 5000 does not like that it starts with a number (1234_DINT). I get the error "Error in member name: Name is invalid".
Has anyone seen a UDT like this, and can anyone explain what the PLC_REG_TO_SEND part would be for? I have seen UDT's like Pump_1.isCalled (bool) and Pump_1.speed (real) or something like that, but never a UDT with two periods or sets of parameters (PLC_REG_TO_SEND.GROUP_15 vs. GROUP_15.1234_DINT[1].0).
Any info on this is massively appreciated. Thank you.
Thanks for your reply, very helpful. I had seen that before and scanned through it, however on your recommendation I went through and set up a Produced tag which I will test when I am back in the office tomorrow.
I guess my one remaining question is this: How is it possible for the member of a UDT to start with a number, as our customer's UDT's do? For example,
PLC_REG_TO_SEND.GROUP_15.1234_DINT[1].0]
has the "1234_DINT" member which starts with a number. According to Studio 5000, this is a no-no, and I am wondering if the tag list we were provided is inaccurate.
I will reach out to the customer tomorrow to confirm, but would anybody know how it is possible for a member object or parameter to begin with a number?
It shouldn't be possible for a tag name, even for a sub-element in a UDT, to begin with a number. Maybe your client found a workaround using overlays or imports or hard-to-see characters, or maybe it's an error in their correspondence with you.
Any time you're doing P/C with complex datatypes, I strongly recommend doing and export/import from the source program to eliminate the risk of typos. The datatypes and element names must match *exactly*.
This is as close as I've ever been to getting a UDT member to start with a number - by preceding it with an underscore:
Overlays do not allow you to use a tagname with a leading number.
The tagnames do NOT have to match although it is standard practice that they do.
Also:
If you are using a UDT with the first member of type CONNECTION_STATUS then the datatypes have to match.
If you are using a UDT without CONNECTION_STATUS then the data types do NOT have to match but the overall UDT size must be the same.
In this case a DINT in the Producer could be read as two INT's in the Consumer...
Good Evening , I'm in the process of retiring a Dell XP Laptop. I'm starting to download RS Logix 5000 version 15 , 16 , 17 etc. Then the...
6,448
Hi... I'm working on a project where we are modifying an existing system. We are adding a 1756-ib32 input card to a spare slot on a existing rack...
2,089
I am new to this company. I am still trying to stabilize my laptop crash . I have 2 Windows XP coming Wednesday. I was digging in some drawers and...
4,082
Hey, Can you guys help explain this to me, I have always seem to get this confused. The question is whats the difference between the Rslogix 5000...
5,198
Does anyone know why CompactLogix L4x Series are not supported with Rockwell's new Studio 5000 Software? My understanding was that RsLogix 5000...
5,553