Rockwell's Pos & Vel PID Forms
Taylor Turner
Sep 2020
Midwest
78
I've got quite a few questions to fire.
In the velocity form, why does the P term now act like the D term in the positional form?
The D term in the velocity form is a nifty equation, but is this an example of second derivative tuning? Can it be extended to n-3?
I just had a hard time explaining to someone that with this velocity form you have to tune I like P and now P like D and P doesn't exist now, but D now does this cool acceleration thing... etc.
Would the attached have redundant terms or would this keep the classic PID understanding?
Do you guys have any resources that have other error terms or algorithm forms?
(Edit) Just to get it out of the way, I know t should probably be squared in that last term.
With the possible exception of how anti-windup is done, roundoff-error in the sixth or seventh decimal place, and how the tuning is done (e.g. Ki vs. Ti, although that is usually a dependent gains vs. independent gains difference), Rockwell's Positional and Velocity forms of the PID equation are arithmetically, and behave, exactly the same.
Cf. this link.
And this link and this link also.
This works because the P term is being integrated.
Yes, this is necessary for underdamped hydraulic systems. The RMC has a second derivative gain which is applied to errors between the target and actual accleration.
Sometimes explaining the difference between the two forms of PID is hard.
drbitboy is correct. The I, P and D gains are tuned the same way and usually provide the same results.
Keep the same understanding.
Again, we have a second derivative gain that is multiplied by the difference between the target and actual acceleration. The problem with this is calculating the actual acceleration
I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
164
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
129
Hello, recently I saw a graphic from any Rockwell App, I cant identify which one is. Attached a SS. Its used to see dashboard from datapoints and...
127
I'm working with a project that contains some routines in ST but mostly in ladder. Am I correct in assuming this 'rung': DB1001DO._01AV55_OPEN :=...
114
I noticed in Rockwell AOIs, they add a BOOL Output parameter at the end of the "Parameters" list of each AOI that carries the same name as the...
79