Rotork Valve (Profibus) Acyclic data development using siemens S7
Feb 2013
Chorley
Hi all,
I could use a little bit of help. I am currently developing a standard block for a Rotork valve which is to communicate to a S7-300 PLC via Profibus. The problem that I am having is that the customer wants to extract more information using the Acyclic features available on profibus.
I have only used basic (standard) profibus functions, so the acyclic element is very confusing.
any help/advise/useful tips on developing acyclic functions or if anyone has had any experience on Acyclic functions for Rotork valves, it would be hugely appreciated.
Cheers
Shane
I will point you in the right direction you can use SFB 52 or SFC 59. RD_REC. There are loads of information available on the siemens website on this. These are used across multiple devices.
Good luck
Many thanks for your reply, I have since been looking at this in depth and found those instructions coming up time and time again. You reply has now confirmed that I am looking in teh right direction. so I am going to have a go with these and see where I get to.
SFC 52 and SFC 59
Hello Shane;
Is the Rotork valve controller a DPV1 slave?
Read_REC and WR_REC instructions will only work if the slave has been programmed to transfer data records acyclicaly, that is, if it has been formatted as a DPV1 slave by the manufacturer.
And of course the DP-master must be DPV1 also (most recent S7 CPUs are).
What model are you using, and does the manual/datasheet specify it as a DPV1 (or DPV0)Profibus-DP slave?
Hope this helps,
Daniel Chartier
I have just managed to locate the manual for DP communications. The does state DP-V1 communications. We are using an S7-318 processor. So I am assuming that this is all very possible. :)
Dear All, I am trying to communicate between GE Fanuc PBM101 profibus master and Rotork actuator simple dual channel type module. I have used...
1,629
Has anyone ever used a PDA to download configurations using IR from the IQ series of Rotork valve actuators? The software is downloadable from...
1,816
I'm fairly new to the world of PLC's. So far I've managed to resolve the problems I've crossed but this one has me stumped. I've got a Rotork...
3,865
We are currently using a number of Rotork IQ valves on a project. The client has a requirement to send/ receive acyclic data from the PLC. This...
1,839
Hi, I am trying to get communication between Siemens S7 400 CPU & Rotork actuator. I have already installed GSD file in HW config and downloaded...
4,021