rs view 32 with 1756 enbt
alex_cordova
Oct 2009
paramount
102
i have read all i can on this in this website, but i need a walk through for setup on node in rs view 32.
i want to know how to setup a opc topic in rs linx for 1756 enbt card
and also set up the node in rs view 32
Alex:
Do you have access to the AB/RA Knowledgebase?
First thing is you don't set up an OPC Topic to an ENBT Card, it has to be to the Processor.
Stu...
no i don't have access to that page
Well, that's too bad, as I probably could have found an article that would have helped you. Ok, lets start with an OPC Topic in RSLinx. There are a number of ways of specifying an OPC Topic. However, one of the easiest is to Navigate to to the PLC Processor you want to set up in the RSLinx RSWho, then Right Click on it, and select "Configure a New DDE/OPC Topic". Give it a sensible name, and leave everything at Default Values for now.
Stu....
Something like this;
Ok, in RSView you set up your OPC Topic under System, then Node. Give it a name, I usually use the same name as the RSLinx OPC Topic, but you don't have to. Then select the OPC Server Radio Button. Under Server select RSLinx OPC Server, and put the OPC Topic from RSLinx in the Access Path. Substitute the relevant name for the OPC_Topic that I used in this example.
Stu....
I have updated the firmware of the EWEB module first to 5.001 then to 4.016. I have updated the firmware of the 1756-L73 to v28. The device is...
1,520
I have a customer with network layout containing DH+ and Ethernet, connected with a 1756-DHRIO module. The network contains several SLCs, Compact...
3,617
Hi Guys, Has anybody used a new L8 processor with FactoryTalk View ME? I try adding the device shortcut and compile the program, it gives me the...
2,255
Hello, I have a problem making a connection whit my PLC and the program factorytalk view studio. When i try to connect to my devices it shows...
10,656
Hello all, May I know how to configure and establish communication between PanelView Plus 1500 with ControlLogix 1756-L71? Figure above showed...
3,296