I got called to do some updates on a pump control panel for a waste treatment system and found a few lines in the running PLC (SLC5/04 1747-L542B) with shorted branches going around the low level floats that should shut off the pumps & mixer.
When I try to verify the file it shows the 4 errors of shorted branches, so why & how would it let the file be downloaded to the PLC, I didn't think this could be accomplished with online edits either. (Does the PLC go through the branch if the float opens? It must as you can see in the attached picture the low level float is off, but the mixer is still running.)
With the output holding itself on & the low level float bypassed this mixer shown would never turn itself off, even if the Messaging PLC dropped the bit or the messaging watchdog timed out?
This project has 3 pumps written the same way, also.
When I try to verify the file it shows the 4 errors of shorted branches, so why & how would it let the file be downloaded to the PLC, I didn't think this could be accomplished with online edits either. (Does the PLC go through the branch if the float opens? It must as you can see in the attached picture the low level float is off, but the mixer is still running.)
With the output holding itself on & the low level float bypassed this mixer shown would never turn itself off, even if the Messaging PLC dropped the bit or the messaging watchdog timed out?
This project has 3 pumps written the same way, also.