RSLinx Ver. 2.59 Communication Fail

endangs

Member
Join Date
Aug 2016
Location
Jakarta
Posts
19
Dear All, I have just experience running RSLinx Ver. 2.59 to connect with ControlLogix 5000 1756-L73 with Firmware rev. 24.11, found: the RSLinx was not recognized the Controller (Logix5000)
Does anyone know what's going wrong ?
 
If you see a yellow question mark in RSLinx, that doesn't have a red X, right click on the yellow question mark, upload EDS from device.
 
RSLinx 2.59 was the last revision of the 2.5x major revision, which had a very long product lifecycle of about ten years.

It *should* still be able to recognize modern 1756-ENxT EtherNet/IP modules and modern ControlLogix controllers, but it would not have their EDS files installed by default.

Right-clicking and selecting "upload EDS", or otherwise loading EDS files from Rockwell Automation using the EDS Hardware Installation Tool should allow RSLinx Classic to recognize any ControlLogix CPU and Ethernet module.
 

Similar Topics

Hey! In my previous queries on how to handle an OPC server like RSLinx in the ArchestrA IDE galaxy, I have succeeded and the answer was to just...
Replies
0
Views
1,821
Hello all, I am using Factory Talk View v9 in order to configure my application. In RSLinx Enterprise Server Properties when I put as Computer...
Replies
1
Views
4,007
Hello there, I am trying to get an ADAM 4561 converter to talk via RS232 DF1 to a Micrologix 1400. I know that some USB/RS232 converters simply...
Replies
0
Views
1,344
Hello. I set up an OPC server using my RSLinx. But I do not know how to access the data from Microsoft Visual Studio with NI measurement studio...
Replies
0
Views
5,632
Hi, I am trying to communicate Siemens MP277 HMI with RSLinx Gateway OPC server. The RSLinx Gateway OPC server is running on a computer. The...
Replies
3
Views
6,247
Back
Top Bottom