RSlogix 5000 find highest value of array
waterbottle
Mar 2019
Florida
42
Hello
Currently have a project in which I have to find the highest value in a dint array. Once the highest value is found I will have to move the Dint tag that holds the highest value. Basically the array holds the amount of jams and I need to display the highest jam location. Each dint of the array is a location and the value is the addition of the number of jams it had. Any ideas will be highly appreciated.
I would program a loop to look at each dint in the array using a pointer. Increment the pointer after every scan or however often you need to check it. Store highest value and constantly compare each check to the highest. Once a new higher value is found, store that pointer's value, which is the element in the array's number.
Remember you can use the pointer inside of the array brackets: myDintArray[pointer]
To find the position of the Highest Value:
Array_Pos_HighestValue:=0;
for i:=0 to 99 do;
if DataArray>DataArray[Array_Pos_HighestValue] then
Array_Pos_HighestValue:=i;
end_if;
end_for;
Mickey,
Not sure that will do what he wants, that will sort the values, but will it tell the tag of the highest value?
Yes, just select the last register in the array after the sort. Ascending order.
See examples page 373 and 374 of pdf I posted.
It is not necessary to sort the array just to find the highest value as destination unknown proposed, a sort will most likely take longer
Why not keep a running max value and update it upon insertion into the array, if the new value is higher than the most recent max?
Beats searching over and over.
Not only is a sort not what the OP ultimately wants, it destroys the information he is really concerned about: which location originally contains the highest number. He is trying to determine what portion of his machine is contributing the most jams. The snippet of pseudocode that destination unknown posted is what you are looking for.
Keith
Keith
Yes this is exactly what I'm trying to do. I tried to sort but it changes the position of the highest value. Each tag on the array represent a jam location portion of an air conveyor that moves empty bottles. The tag is the sum of the jams in that section. Trying to have like a pointer that indicates which tag in the array has the highest value.
Example
JamArray[0] = 4
JamArray[1] = 10
JamArray[2] = 3
JamArray[3] = 2
I will then need to indicate that JamArray[1] is the highest value
Why not just put the Jam locations names stated on a HMI screen, with the corresponding registers next to it, and read it out.
The space is limited since is just one display screen used to spot jams in the lines for the operator to unjam with no touch capability for them to change pages. The Idea is to get the highest value and indicate the position then that value will indicate the location name in the hmi.:unsure::unsure::unsure:
I'm troubleshooting a customer's machine, and I've been racking my brain trying to figure out an answer to a question of where a value is being...
22
3,329
Hey all, So we have had this piece of equipment for a while but its a question that always blows my mind away when troubleshooting this piece of...
1,458
In Rslogix 5000, when searching for tags, is there a way to look only for destructives? Thanks.
3,962
When i do the find all search from the drop down menu, it will do the search but the pop up box that shows all the found search's wont pop up...
1,798
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
157
