RSLogix 5000 - Message (MSG)
bernardow1
Nov 2022
Sao Paulo
17
I'm trying get information from another same PLC
PLC1: CompactLogix 1769-L16ER-BB1B (192.168.0.133)
PLC1: CompactLogix 1769-L16ER-BB1B (192.168.0.135)
But, i receive this errors...
Error Code: 16#00FF
The screenshots below is my config...
Any help?! Thanks guys!
Captura de tela 2023-08-24 144732.png Captura de tela 2023-08-24 145124.png Captura de tela 2023-08-24 145218.png Captura de tela 2023-08-24 145346.png
The problem may be on your last screen shot it says Identity: Mismatch
You may have to make sure they match or just disable keying.
Keying is disabled, see the previous screenshot.
EDIT: This is not to say that the mismatch is necessarily unrelated. If the message is treating it as a different module from what it actually is because of the mismatch, I could see that difference resulting in an error.
Vars:
Bool (Other PLC) FUNDO_ABERTO
DINT (This PLIC) FUNDO_ABERTO_CT1
Message (This PLIC) MSG_DI_DESCARGA_CT1
The two CompactLogix have the same operation, I have a total of three CompactLogix that control the same machines, but I need to get specific information from each of them and the variable "FUNDO_ABERTO" I have declared in both CompactLogix
Captura de tela 2023-08-25 080435.png Captura de tela 2023-08-25 080527.png Captura de tela 2023-08-24 144732.png
I discovery other error:
When i click on Properties in the other PLC on Ethernet... appears for me this error, on the ab Internet Protocol
Tags needs to be same type & no BOOL.
It is impossible to do that, "Message" does not accept returning the variable to type Bool. I already tried it and it doesn't even let me save the configuration...
When i use BOOL, RSLogix show me this error "I am getting the error "Message references a tag of BOOL data type."":
http://www.plctalk.net/qanda/showthread.php?t=114987
ControlLogix does not support the BOOL datatype in a MSG instruction. It never has.
This was specifically done to prevent users from wasting bandwidth and memory and complexity to transfer individual bits of data instead of packing them into a structure or INT/DINT.
What? I love wasted bandwidth.
Well, that and no one seems to agree on how much memory a BOOL consumes.
Rockwell: 1 byte
Rockwell UDT: ZZZZZZZZ_stuffThemIntoHere and make ZZZZZZZZZ_stuffThemIntoHere2 after 8 BOOL
Omron: 2 bytes
ARM Cortex-M0: sorry, segfault for addressing less than 4 bytes
The path you are using... is that OK?
I've never added one to the IO tree like that and seeing it missing the backplane, slot in the path always gives me pause.
I know a few CPLX don't require that, but just throwing it out there.
Hey guys, Ok i have a few stud welders at work. I just added the logic to count the cycles on the weld head and after x ammount of cycles the...
4,176
Hi. This is my first post. I am trying to configure a message block in 5000, Release 13 and I get a response that states that the instruction...
2,136
I loaded Rslogix 5000 software on my xp operating system and everything was fine. I then loaded FactoryTalk View Site Edition and it required me...
43,328
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
158