RSView 32/FactoryTalk View Auto Screen Switching

BillRobinson

Member
Join Date
Oct 2006
Location
Sydney, Nova Scotia
Posts
185
Does anybody know how to automatically switch screens for a panel-view application triggered on an alarm?

For example automatically jump to the conveyor screen if a the belt alarm occurs in the PLC?
 
Open up global connections and go to the display tab. You will have to setup a tag for Remote Display Number.

You should make sure that all your screens have unique Display Numbers.

Remember in your PLC logic to always put that tag back to zero. This will give control back to the user.
 