RSViewME (3.2) Invalid Expression Error
automatic
Aug 2004
136
I am getting an Invalid expression error on tags that I try to use bitwise operators. I found the Rockwell technote - E50265342 - Invalid Expression: Invalid Floating Point Operation - did what it says, but I am still getting the error.
I am converting the application from a 1400e with Block transfers.
Thanks!
Rockwell Technote
Last Modified: 07/02/2003
General Category:
sHMI (Visualization)
Product(s):
RSView Machine Edition
Catalog #:
Series / Revision:
3.0
Symptoms (Keyphrases):
Problem:
Expression causes a diagnotic error message and the expression does not work.
Cause:
This is caused by using bitwise operators with a Default data type in an HMI tag
Verify:
A diagnostics errror message is created when the display is opened at runtime, or the display is test run in RSView Studio.
Cure:
Use direct reference tags or change the HMI Tag data type to an integer data type.
Prevention:
Always specify a data type when creating integer HMI tags. This is automatically done if the Tag Browser is used to select tag addresses.
Problem
"Unable to activate connection"
"Invalid expression: Invalid floating point operation"
Cause
This is caused by using bitwise operators with a Default data type in an HMI tag. Bitwise operators are only valid for integer tags. The default data type means that the HMI tag can act as a floating point tag or an integer tag.
Example expression: Tag & 3
Solution Use direct reference tags or change the HMI Tag data type to an integer data type. This can be easily done by exporting the tag database to a CSV file (Tag Import/Export Wizard) and then changing all the required tags to Integer data type (Change column H "Native Type" to an uppercase i "I" for each required tag). Once this is done, import the CSV file back into the ME application. You will need to restart RSView Studio before the tag changes are updated.
Solved
Apparently, closing and opening RSView Studio is not enough. A re-start of the computer fixed the problem, after doing what the technote says.
Does anyone know if there is a way to bypass the 100 tag limit on logging data in a FactoryTalk View ME - Data log Model? I am under the...
2,386
Is there any way to run RSViewME Station in "full screen mode" On a PC? OR Do I have to modify the application to match the screen resolution of...
2,062
I loaded a new *mer file into a RSViewME PanelView and now when the PanelView starts up it looks for a external memory card. I loaded the file...
2,045
Hi everybody I got one panelview 1000 plus running, my client want to transfer same application from panelview to a PC, same time they want...
2,088
I have an integer that the PLC-5 processor is feeding the panelview 1250. Is there any way to have RSview ME convert this integer to hex? It is...
4,680