Hello

how are you all? I have a problem with RTD pt100.I have CPU 315 with analog module SM331 AI 2*12bits how to program it for temperature??
 
Sorry PLC is from siemens CPU 315 I have install in our system.just to know how to program for RTD pt100 means for temperature control.??
 
Well, the temperature sensor you have doesn't have a 4-20ma or -10 to 10V output. It's an RTD, I believe you'll need a device in between to connect the RTD to, then the output of that will go to your analog input card.

Or, I believe Siemens sells RTD input modules.
 
Sorry again the temperature sensor have 4 to 20ma output i connect and call FC105 scaling module its working now but i can not see real temperature want to put Low limit 0 and high limit 80 degree how to set that values????
Thanks for your time all
 
I think your problem is that the PT100/4-20mA converter is set up for 0-100ºC (or something else), not 0-80ºC. You have two choices: the easiest, is to scale the program in the PLC from 0-100ºC or then you have to reprogram the PT100/4-20mA converter for a 0-80ºC. The converters can be reprogramed by dip switches, welded jumpers or by a special software.
 

Similar Topics

Hello and thank you to all of you who volunteer your time to help others. I have a question about 100 Ohm Platinum RTDs. Using this with an...
Replies
4
Views
3,152
Hi friends I got a PT100 Ohm RTD Automation Direct part number RTD0100-10-010-H .How in this case would I connect the RTD to a 3 wire device...
Replies
10
Views
4,859
how to calibrate RTD PT100 to work with fatek plc and what is the best type for sensitive range from 0 to 100 C. i want to work on analog module...
Replies
39
Views
11,396
Hello to all, my name is nagaraj from Bangalore, Actuall i have a RTD PT100 2 wire type and it is fixed 30 meter away from the PLC panel,So...
Replies
1
Views
3,166
Is it possible to use a 3 wire RTD with a Siemens Analog input card without having to linearize the signal prior to the module? The card can be...
Replies
1
Views
7,315
Back
Top Bottom