S7-1200 PID issue
eastnder
Aug 2013
Hawaii
I'm using a S7-1200 1214 CPU with version 10.5 TIA software to control a chilled water loop- but even with compact PID instruction enabled and everything working the analog output has no effect in auto. If I put the PID DB in manual it operates the modulating valve (4-20mA output) fine. In the PID loop tuning screen the output seems to operate OK too, and there are no fault codes- anyone have ideas on possible issues? I'm about ready to yank the processor and put in something else.
Its a chiller loop, so in this case the PID output is inverted. The PID monitor shows its trying what I want it to do....
TIA10.5 PID was a pain in the backside. You seemed to have to go through the auto tune system and then enable the loop before it worked. TIA has no gone through V11 and is up to V12, so an upgrade my be a good idea.
Otherwise have a look here:
https://www.automation.siemens.com/...ng&ForumID=265&Language=en&onlyInternet=False
It is the Siemens official forum, you will find lots of stuff on the old PID. If you upgrade to T11 or better you could look at various alternative PID loops available on the site. You will also find a lot of people complaining the we have turned in to the TIA Beta testers.
Hello all, I have set up a PID loop which works fine except it is a bit slow during the startup. I wish that it would reach near the setpoint...
1,852
how can i use pid+pwm to control brightness of the ac light
2,263
Hello everyone, this is my tutorial for using PID function on S7-1200. Hope you guy like it. https://www.youtube.com/watch?v=INB6_7SqeOg
1,645
Hello everyone, I'm new in using plc software. I want to set a parameter for my centrifugal pump using an i/p from PID block so that the range of...
1,292
Hello, I changed controller type in RSLogix 500 from SLC 5/02 to MicroLogix 1200 and was given the ladder logic to update it for the new...
25
4,872