s7-1200 startup processing

adam_lhadi

Member
Join Date
Feb 2022
Location
algeria
Posts
59
in s7-1200 manual it said
Whenever the operating mode changes from STOP to RUN, the CPU clears the process image inputs, initializes the process image outputs and processes the startup OBs. Any read accesses to the process-image inputs by instructions in the startup OBs read zero rather than the current physical input value. Therefore, to read the current state of a physical input
during the startup mode, you must perform an immediate read

so, in OB100 i have put (pic) ,i didnt preform an immediate read ": p" also the physical input is energized(24V) so the Q output should not be Set because the CPU cleared the process image input
but the Q output on (according to the Paragraphe) it should not
where i am wrong

Kind regards

ob100.PNG
 

Similar Topics

Hello all, I have set up a PID loop which works fine except it is a bit slow during the startup. I wish that it would reach near the setpoint...
Replies
1
Views
1,837
Hello, I have a question about an encoder that has absolute measurement. Specifically, it's the Lika SMA5, which I would like to connect...
Replies
2
Views
54
Hello, I have a question about an encoder that has absolute measurement. Specifically, it's the Lika SMA5, which I would like to connect...
Replies
0
Views
31
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
267
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
91
Back
Top Bottom