S7-200 to TP177 Cable

Alejin

Member
Join Date
Apr 2007
Location
Santiago
Posts
9
Hi I need to connect an S7-200 to a TP177micro operator panel peer to peer but the communication cable is not available in my supply company.



I was reading that both ports (PLC & HMI) are RS485 so I think that I can make my own cable but I don’t know the pinout. Anybody can give me this information?



Thanks
 
Alejin said:
Hi I need to connect an S7-200 to a TP177micro operator panel peer to peer but the communication cable is not available in my supply company.



I was reading that both ports (PLC & HMI) are RS485 so I think that I can make my own cable but I don’t know the pinout. Anybody can give me this information?



Thanks

Both Sides:

PIN 3 - 3
PIN 8 - 8
PLUS Shield to PIN 5

Nick

TP177M.JPG
 