S7-300 Defective PLC when going online, PLCSIM too...

adfox

Member
Join Date
Jun 2006
Location
Poland
Posts
334
Hi I've got very strange problem.
I have a project for CPU 317-2 DP.

1.I download hardware config to PLC - it's ok.
2.I download OB1 with contents

L 0
T MB2 - it's still OK.

3.I go online in OB1 - PLC stops and diag buffer says PLC Defective.

This happens in PLCSIM (5.4+SP6).

I've found this in diag buffer (attached):

Code:
Event 9 of 10:  Event ID 16# 530D
New startup information in STOP mode
Startup prevented by:
Loading user program or internal inconsistency detected
 (SDBs less than 200 incomplete, superfluous, or incorrect)
- STOP request exists
- Keyswitch set to STOP
- Cold restart or warm restart necessary
Startup information: 
- Time for time stamp at the last non backed up power on
- Single processor operation
Current/last startup type:
- No startup type/following memory reset
Permissibility of certain startup types: 
- Manual startup not permitted, corrections in parameter assignment, submodule, etc. necessary
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- No startup type/following memory reset
Operating mode: STOP (internal)
Incoming event
07:47:42.668 PM  08/01/2016
(Coding: 16# 530D  FF04  C777  0161  0000  1100)

How can I find the source of error ?
I'm linking the project file to dropbox as it's quite big multi-PLC (5 MB).

https://www.dropbox.com/s/9usdb4utvxi1bs0/Calc_6.14.zip?dl=0

It's the plc named Sivacon.

I'm really confused. I'd be really glad if someone could point me in the right direction.
 
Recompile your hardware config, then download it again.
Make sure no monitor functions are active when you do the download.
Then download your program blocks.
 
Hi, did this numerous times already. Recompiled hw, netpro and existing software ( not called since empty OB1 alone is enough for PLC to die ).
 
Last edited:
The error / diagnostic message indicates inconsistent system data.
This can be caused by downloading hardware with a debug (monitor) function active.
 
No online functions active, more over after plc sim dying - i need to close it and open it again as it stops to function, with real PLC i need to take power down, and power it up in stop mode to be able to download again.
 
Ok, then post an archive of your project.
What are the versions of your software andthe OS?
 
Link to the project is in the fist post ( dropbox ) as it's too large to fit forums limit.

Windows 7 SP1 64
Step 7 5.5 + SP4
PLCSim 5.4 + SP6

Thank You.
 
Have you tried to rebuild the hw from scratch in a new project?

It might be an evil ghost hiding in the old configuration
icon12.gif
.

Kalle
 
Not sure if this is good news or bad -
The project also causes
I am on Win 7 / 64 bitmy PLCSIM to crash.

Step 7 V5.5 SP4 and PLCSIM 5.4 SP5.
 
Download HW + OB1 and enter online in OB1 - instant crash.
KalleOlsen : Doing it right now - its 128 dp slaves to copy paste ;)))
 
Last edited:
2 DP networks on PLC, 2 additional CP 342-5 and 2 343-1 ethernet cps.

Ok... i've mostly copy-pasted slaves from defective project, added CPs with copy-paste,
manually created connections in netpro - and it works like nothing happened.

Thanks for investigating - but I still don't know what caused this behaviour.
 
Ok, i've found the solution.
It can be used as a nice job interview puzzle.

1st screen - my CPU properties, notice Process Image size.
2nd screen- my DP network, I had to add 2 new 3WL circuit breakers, so as my first 3WL was at PIW/PWQ 300 and first simocode on 512, i added them up front.

And voila.
Thanks for the help :)

Cpu_Prop.png cpuNetwork.jpg
 

Similar Topics

Hi all In one of my machine the S7 300 64 KB ( 6ES7953-8LF20-0AA0) micro memory card got defective . I already done mmc reset but still issue...
Replies
1
Views
1,963
Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
111
So basically i have 2 queries : 1. I have a program file of S7-300 PLC which i want to migrate in RSLogix500.In short i want to convert my simatic...
Replies
15
Views
256
Hi i using Kinetik 300 2097 driver control by EIP with using move absolute and incremental for motion , but i want to add same driver and motor as...
Replies
0
Views
64
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
63
Back
Top Bottom