S7 300 EPROM replacement

Join Date
Oct 2020
Location
Bangladesh
Posts
2
Dear All,
I have an S7 300 damaged CPU. I don't have it's backup program. I want install a new CPU. If I replace the new CPU internal EPROM with the old one then will it work as before? As I don't have backup program so I want to replace the programmed IC. But I don't have idea which one is the program IC or EPROM.

Looking for your help.

Thanks
 
What type nos exactly of both old and new CPUs ?

If by 'internal EPROM' you mean the MC or MMC flashcard, then yes. If you insert the flashcard in a new but same type no CPU, it shall work again.

If you mean one of the ICs on the circuit board inside, then no. The program is not on an internal EPROM. The program is in the MC or MMC flashcard, or in case of an old-style S7-300 with MC slot, it could be in battry backed RAM.


There is one exception though. I remember that there was a very low end CPU in the old style only with an internal EPROM, S7-312IFM I think.
But I think it is next to impossible to source a new 312IFM CPU.
 

Similar Topics

Hi Group, Please correct me if Im wrong. Memory Card FEPROM serves as LOAD MEMORY that contains configuration file and user progam. Since...
Replies
0
Views
5,283
Our resident Siemens guy is taking the day off today. I was asked if the S7-300 processor allowed one to write to the EEPROM. I am guessing that...
Replies
3
Views
2,745
So basically i have 2 queries : 1. I have a program file of S7-300 PLC which i want to migrate in RSLogix500.In short i want to convert my simatic...
Replies
3
Views
54
Hi i using Kinetik 300 2097 driver control by EIP with using move absolute and incremental for motion , but i want to add same driver and motor as...
Replies
0
Views
54
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
45
Back
Top Bottom