S7-300 PLC in stop using PQW or PIW

No
You don't need another CPU
Lets figure out what's wrong with your dp reads and writes sfc14 and 15

What error do you get?
 
You need to use sfc 14 and sfc 15 for 10 pd.

sew has example on their site if that is too difficult otherwise.
 
Last edited:
IT IS WORKING!!!!!!!!!
Thank you for all the help.
Range adress from 256 is not working, but range from 88 dec is working.
The SFC14 and SFC15 is also working (didn't expected).
See attachment!
Again: Thank you guys for the help!

Greetings,

mulderm
 
In siemens you need to use sfc's for other than 1,2,4 byte lenghts of consistent data. I wonder how is 256 not working but 88 is..
 
Last edited:
Good
Now make a nice reusable function block out of it.

I also wonder why 256 doesn't work unless his analog module uses that address
 
Last edited:

Similar Topics

merry christmas and happy new year i have a click c0-00dr-d and allen bradley 2711c-t3m. can the panelview talk to the click plc via modbus...
Replies
1
Views
229
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
Replies
3
Views
699
Hi Any one here please helpmein simulation of s7 300 plc program with factory io. how to connect. plcsim 5 doesnot have option of s7 300 ..:
Replies
2
Views
1,015
Hello, I have a bit of a situation, and I think I know the answer but this font of knowledge may prove something. I want to do the unthinkable...
Replies
6
Views
2,184
hello guys, I'm trying to establish a connection between Indusoft 8.0 & simatic Plcsim but I keep getting the following error: error...
Replies
3
Views
1,362
Back
Top Bottom