S7-300 S_ODT BI value

Holmux

Lifetime Supporting Member
Join Date
Oct 2013
Location
Aalborg
Posts
279
Hi All

I am working in an old 300 PLC and need to display a few values from timers onto a Basic HMI.

I display the BI values from 4 different S_ODT timers, I split the values into minutes and seconds and sends it off to the HMI, so far so good.

But if my TV value gets dovn to 1 minute or less I get milliseconds in the BI value as well.

My question is if there is an easy way to filter this out or do I need to change my filter depending on the TV value ?

Thanks
/Holmux
 
How are you splitting the time into minutes and secs?


See attached for how the time is stored.

s5time.jpg
 
Last edited:
There is a library block that will convert #s5time to #time - you can convert #time to minutes and seconds.

lib31.jpg
 

Similar Topics

in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
4
Views
112
Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
120
So basically i have 2 queries : 1. I have a program file of S7-300 PLC which i want to migrate in RSLogix500.In short i want to convert my simatic...
Replies
15
Views
282
Hi i using Kinetik 300 2097 driver control by EIP with using move absolute and incremental for motion , but i want to add same driver and motor as...
Replies
0
Views
66
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
81
Back
Top Bottom