Folks,
I have a S7400 PLC with a CP 443 and link with a HMI software.
Is that possible that if i added another CP 443 as redundant
to HMI communication?
Regards
Yes, it is possible to communicate with S7 PLC via several links at the same time even from one HMI.
But if you have one PLC and only one HMI station, you are not on the right way...
The existing CP443(ethernet) have connected to HMI, we just suggest
add another cp443 ( ethenet) as standby comm. What we want is, once
the existing CP 443 was down , the HMI will automatically poll the
data from second cp443.
Mr Geogoyg, what do you mean by not the right way...
Best Regards
Why do you need redundancy between the HMI and the PLC?
The redundancy you are specifying only covers the CP card itself (which should be very resiliant) and the ethernet cable, so I would presume you would run the two cables a totally different route, as cable redundancy is installed to protect against damage to cable, which is normally caused by something cutting through it, so running them together would be self defeating.
But why make such redundancy? Redundancy is normally to protect the process, nice to have redundancy to the HMI but in most cases the HMI can be overidden by the tech's to get things moving. Its more common to have redundancy for the PLC and the process I/O.
Perhaps that is what gregoryg was referring to?
Yes Peter it is what i tried to say.
But if redundancy in HMI is needed than the best solution is to use two HMI's. They should be connected through independent links to the PLC and (of course i they are capable to) each one of them can use another HMI as backup path for connection to PLC (something similar to data gateway).
I am troubleshooting the setup of UDP broadcast receiving on a CP443-1 CP card. The telegrams appear in WireShark with IP 192.168.1.255 Port 7551...
2,303
Hi I have a system where essentially i am connecting an HMI via a switch to the CP443 card. I've set an IP address in the PLC end and an IP...
1,562
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
51
I have a micro1400 processor running two routines (transfer compression/compression molding press). Recipe parameters are stored from job to job...
54
Is there anyone who can help me regarding this HMI is missing the choices when I make a new Device in TIA. Only 7" Display above are the choices...
82