What is the best way to set up a master/slave relationship with an S7-400 Master (Step 7 5.5) and S7-1500 Slave (TIA Portal) PLC?
I could find an example here, but it's specifically for failsafe PLC's.
The Siemens support document above has a more general discussion of i-device, besides the safety setup (which has a few complications). Basically the steps are to:
configure the I-Device transfer areas in the 1500 (device)
Export this I-Device as a GSD
Import it into the 400 (Controller)
The assigned IO addresses can be whatever is desired, they do not have to match.
Many thanks! I will try that method. The link Siemens provided for "config_idevice_standard_DOCU_V1d0_en.pdf" is broken, do you happen to have the pdf file?
Many thanks! I will try that method. The link Siemens provided for "config_idevice_standard_DOCU_V1d0_en.pdf" is broken, do you happen to have the pdf file?