Shaikh Mostafa Ali
Member
Hello All siemens expert
Here I have attached two file (1) about port setting (2) server setting. Again I mention all those in brief:
A. about SCADA computer:
(a) Hardware:
- Dell Power edge T300 (server)
- Dual port Ethernet card (Intel (R)PRO/1000 Server Adapter)
- Dual port Ethernet card (Broadcom Net Xtreme Gigabit Ehernet)
- Matrox Plug & Play multi monitorcard ( single DVI port) (M9120 Plus LP PCIe X1)
- 2 Monitor connected through a parallel branch cable to the single DVI port of Matrox card
(b)Software Installed on SCADA computer (server):
ComputerDescription:BioWoodServer
ComputerName:5028_SCADA
WorkGroup:WORKGROUP
-MS WINDOW 2003 R2 STANDARD EDITION ,SP2 V 5.2
IP Address :192.168.0.113
Subnet mask :255.255.255.0
Default Gateway :192.168.0.2
(Network Connection Details)
Physical Address :00-15-17-B8-51-C4
IP Address :192.168.0.113
Subnet mask :255. 255 255 .0
Default Gateway :192.168.0.2
DNS Server :192.168.0.1
WINS Server :
Here I have attached two file (1) about port setting (2) server setting. Again I mention all those in brief:
A. about SCADA computer:
(a) Hardware:
- Dell Power edge T300 (server)
- Dual port Ethernet card (Intel (R)PRO/1000 Server Adapter)
- Dual port Ethernet card (Broadcom Net Xtreme Gigabit Ehernet)
- Matrox Plug & Play multi monitorcard ( single DVI port) (M9120 Plus LP PCIe X1)
- 2 Monitor connected through a parallel branch cable to the single DVI port of Matrox card
(b)Software Installed on SCADA computer (server):
ComputerDescription:BioWoodServer
ComputerName:5028_SCADA
WorkGroup:WORKGROUP
-MS WINDOW 2003 R2 STANDARD EDITION ,SP2 V 5.2
-MS SQL SERVER 2005 V.090.3042.00
-WONDERWARE INDUSTRIAL SQL SERVER V 9.0.000
-WONDERWARE APPLICATION SERVER V 3.1 .000 3113.0001.0.0000
-WONDERWARE ACTIVE FACTORY V 9.2.0.0, 355.0112.0.0000
-WONDERWARE INTOUCH V 10.1 1412.0130.000.0000
-WONDERWARE S7SIMATIC DASERVER V 1.5 .100
-WONDERWARE SIDIRECT DASERVER V 1.5.100
-KEP SERVER FOR WONDERWARE V4.300.449.3-U
-OPC QUICK CLIENT V4.86.109.0-U
-OPEN OFFICE -ORG 3.1 V 3.1.0
- MATROX POWER DESK -SE V 11.12 .0000.0045
-WONDERWARE INDUSTRIAL SQL SERVER V 9.0.000
-WONDERWARE APPLICATION SERVER V 3.1 .000 3113.0001.0.0000
-WONDERWARE ACTIVE FACTORY V 9.2.0.0, 355.0112.0.0000
-WONDERWARE INTOUCH V 10.1 1412.0130.000.0000
-WONDERWARE S7SIMATIC DASERVER V 1.5 .100
-WONDERWARE SIDIRECT DASERVER V 1.5.100
-KEP SERVER FOR WONDERWARE V4.300.449.3-U
-OPC QUICK CLIENT V4.86.109.0-U
-OPEN OFFICE -ORG 3.1 V 3.1.0
- MATROX POWER DESK -SE V 11.12 .0000.0045
(c) Ethernet Connection
- cable: normal LAN cable 4 pair 24AWG UTP patch cable (for just testing purpose)
- PLC 1st port connected to Intel Ethernet card port 1
- Port Settings:
Address T ype :Manually Configured.- cable: normal LAN cable 4 pair 24AWG UTP patch cable (for just testing purpose)
- PLC 1st port connected to Intel Ethernet card port 1
- Port Settings:
IP Address :192.168.0.113
Subnet mask :255.255.255.0
Default Gateway :192.168.0.2
(Network Connection Details)
Physical Address :00-15-17-B8-51-C4
IP Address :192.168.0.113
Subnet mask :255. 255 255 .0
Default Gateway :192.168.0.2
DNS Server :192.168.0.1
WINS Server :
(B) About PLC (S7)
(a) Hardware:
- Rack:0 Slot:1 =PS405 4A
Slot:2=CPU 414-3
Slot:3=CP443-1 (Dual Port Ethernet)
(b)In Simatic Manager/HW configuration/setting
Properties CP443-1 (R0/S4)
Under Tab: IP access protection
Activate web server = checked
Activate Access protection for IP communication= unchecked
Under Tab: IP Configuration
Set IP address in Properties-Ethernet Interface and dialog=checked
Obtain Ip Addres From DHCP=Unchecked
Set IP address in user program=unchecked
Set Ip address in different method=unchecked
Under Tab :Addresses
Start:8188
Address setting for lock/unlock with fetch/write speed send receive=unchecked
Under Tab :Options
Protection level: Notlocked
Activate Fast Switchover connection=unchecked
Interval=30
Disable UDP frame buffering=unchecked
Match case=unchecked
Under Tab :Time day synchronization
Activate NTP time day synchronization=checked
Time day sychronization on full minute=checked
Forward time day to station=checked
NTP server Address= 192.168.0.113
Propertise -PN-IO (R0/S4.1)
Under Tab:Genaral
Device Name: PN-IO
Support Device Replacement without exchangebale medium=checked
Interface: Type: Ethernet , Device number: 0 , Address 192.168.0.130, Networked : yes
Under "Properties":
Set MAC adddress/ use ISO protocol=checked
MAC address:00-0E-8C-BB-68_98 ( as printed on CP )
IP prototcol used=checked
IP address:192.168.0.130
subnet mask:255.255.255.0
Gateway: do not use router =checked
Subnet: highlighted on: Ethernet(1) , Properties: Name: Ethernet(1),
S7 subnet ID: 008A - 0053
Under Tab:Address
Interface;8187
Under Tab:Profinet
Send clock:1.00 ms
Max. allocation profinet IO:0.0 %
OB 82 /I/O fault task - call at communication interrupt=unchecked
Under Tab:Synchronization
Sychornization role: not synchronyzed
Name of sync domain:syncdomain -default
RT class: RT;IRT
IRT option:-----
Under Tab:Media Redudancy
Domain:mrpdomain-1
Role:Not node in the ring
Properties PN-IO-port 1(ro/s4/x1/p1)
Under Tab:Genaral
Nameort 1
Addresse, port:8186
Under Tab:Topology:
Partner port :any partner
Under Tab:Options
Transmission medium: Automatic setting
Boundaries all are unchecked
For port 2 properties : almost as port1
(c) In Net Pro
Properties TCP connections:
Under Tab:Genaral Information
ID(hex): 0001 A050
Name :TCP connection1
Active connection Establishment=checked
Addresses: Local , IP:192.168.0.130 ; port (dec):2000
Remote,: 192.168.0.113 port (dec):2000
Under Tab:Options : Mode:Send/receive
Under Tab:Overview , everything is as befor , status :OK
(a) Hardware:
- Rack:0 Slot:1 =PS405 4A
Slot:2=CPU 414-3
Slot:3=CP443-1 (Dual Port Ethernet)
(b)In Simatic Manager/HW configuration/setting
Properties CP443-1 (R0/S4)
Under Tab: IP access protection
Activate web server = checked
Activate Access protection for IP communication= unchecked
Under Tab: IP Configuration
Set IP address in Properties-Ethernet Interface and dialog=checked
Obtain Ip Addres From DHCP=Unchecked
Set IP address in user program=unchecked
Set Ip address in different method=unchecked
Under Tab :Addresses
Start:8188
Address setting for lock/unlock with fetch/write speed send receive=unchecked
Under Tab :Options
Protection level: Notlocked
Activate Fast Switchover connection=unchecked
Interval=30
Disable UDP frame buffering=unchecked
Match case=unchecked
Under Tab :Time day synchronization
Activate NTP time day synchronization=checked
Time day sychronization on full minute=checked
Forward time day to station=checked
NTP server Address= 192.168.0.113
Propertise -PN-IO (R0/S4.1)
Under Tab:Genaral
Device Name: PN-IO
Support Device Replacement without exchangebale medium=checked
Interface: Type: Ethernet , Device number: 0 , Address 192.168.0.130, Networked : yes
Under "Properties":
Set MAC adddress/ use ISO protocol=checked
MAC address:00-0E-8C-BB-68_98 ( as printed on CP )
IP prototcol used=checked
IP address:192.168.0.130
subnet mask:255.255.255.0
Gateway: do not use router =checked
Subnet: highlighted on: Ethernet(1) , Properties: Name: Ethernet(1),
S7 subnet ID: 008A - 0053
Under Tab:Address
Interface;8187
Under Tab:Profinet
Send clock:1.00 ms
Max. allocation profinet IO:0.0 %
OB 82 /I/O fault task - call at communication interrupt=unchecked
Under Tab:Synchronization
Sychornization role: not synchronyzed
Name of sync domain:syncdomain -default
RT class: RT;IRT
IRT option:-----
Under Tab:Media Redudancy
Domain:mrpdomain-1
Role:Not node in the ring
Properties PN-IO-port 1(ro/s4/x1/p1)
Under Tab:Genaral
Nameort 1
Addresse, port:8186
Under Tab:Topology:
Partner port :any partner
Under Tab:Options
Transmission medium: Automatic setting
Boundaries all are unchecked
For port 2 properties : almost as port1
(c) In Net Pro
Properties TCP connections:
Under Tab:Genaral Information
ID(hex): 0001 A050
Name :TCP connection1
Active connection Establishment=checked
Addresses: Local , IP:192.168.0.130 ; port (dec):2000
Remote,: 192.168.0.113 port (dec):2000
Under Tab:Options : Mode:Send/receive
Under Tab:Overview , everything is as befor , status :OK
I am not able to communicate with my PLC and little bit confused about the setting of ArchestraA IDE. Can some body guide me to about the setting of Archestra IDE or SMC and making the communications?
I am able to PING my PLC IP from the SCADA computre.