S7 Connection aborted!!

FAGARCIA

Member
Join Date
Sep 2007
Location
ONTARIO
Posts
45
Hello people.
Iam getting the following error.
connectionabort.JPG

I clikc ok and try again and it works for a short period of time.
I'm using PC adapter USB type with this configuration:
pcad.JPG

the plc has this configuration:
hwrmpi.JPG

Any ideas of why I get disconnected so often??

thanks
 
Ideas:
Extreme noise.
No ground.
The USB adapter may be defective.
The MPI port may be defective.
The cable may be defective.
There may be a conflict on the PC with the USB adapter and some other device.
If the PC is supplied from another source than the PLC: Too big voltage difference on the "ground" of the two systems.

Things you can try:
Switch to DP and go online via the DP port.
Change the S7 CPU.
Change the USB adapter.
Change the PC.
 
If nothing more is connected to the MPI port, set the "only master on the bus" flag of the PG/PC interface. This may help also.
 

Similar Topics

Hello guys i'm working with an s7 1200 plc with an ET 200S expansion module. The problem is that i can't find the plc when searching in the...
Replies
1
Views
99
I have got an Rockwell PLC 1769-L36ERMS . I have assigned a IP address to it . But every-time I Reboot the PLC it looses Communication to my PC...
Replies
1
Views
99
Hello all! So I have one project with a S7-1214 and a MTP1500 "Project1" and one project with another S7-1214 "Project2". Both of these PLC:s need...
Replies
6
Views
136
Hi dear . I have a system with cj1m cpu11 etn. previously NT 5z HMI was connected with plc. recently my old HMI got damaged. I want to replace it...
Replies
12
Views
306
Hello gentlemen, Im working on a small project on TIA Portal, about establishing a Modbus TCP connection between my ET200SP plc and a socomec...
Replies
12
Views
352
Back
Top Bottom