S7 IEC Timers
TurpoUrpo
May 2008
Switzerland
1,571
Hi
I did quick hacks for TP and TOF to get reset functions in them. Here is the source:
Code:
FUNCTION_BLOCK TPR
TITLE = Resettable Pulse Timer
VAR_INPUT
  IN, R: BOOL;
  PT : TIME;
END_VAR
VAR_OUTPUT
  Q : BOOL;
  ET : TIME;
END_VAR
VAR
  STATE : BYTE;
  R_Edge : BOOL;
  STIME, ATIME : TIME;
END_VAR
BEGIN
NETWORK
TITLE =
A R;
FP R_Edge;
JCN nres;
L B#16#00;
T STATE;
nres: UC SFB 3;
END_FUNCTION_BLOCK
FUNCTION_BLOCK TOFR
TITLE =   Resettable Off Delay TIMER
VAR_INPUT
  IN, R: BOOL;
  PT : TIME;
END_VAR
VAR_OUTPUT
  Q : BOOL;
  ET : TIME;
END_VAR
VAR
  STATE : BYTE;
  R_Edge : BOOL;
END_VAR
BEGIN
NETWORK
TITLE =
A R;
FP R_Edge;
JCN nres;
L B#16#00;
T STATE;
nres: UC SFB 5;
END_FUNCTION_BLOCK
I looked into making also retentive timer types, but could not find where does ATIME get its value from, has anyone of you found it?
I made one version using SFC 6. And updating STIME while timer was "paused". But I dont think its good way to do it.
Isnt this from the same place as TIME_TCK?
To answer my own question YES..
ATIME is actual time (System time)
STIME is started time
Be aware that the system time has a max value of 2147483647 then it starts at zero ..
Hmh o_O, im sure i tried it, but only in simulator. That was my first guess on where it does get its time from.
Need to try again.
I've used the following timer code in S7-300's for a long time. When migrated to an S7-1500 plc, the timer behaviour changes so that I no longer...
22
5,403
I've tried to add an "s" after the tag for the PT value of an IEC timer but it's rejected, even if the tag type is "time". As the timebase is ms...
2,127
Hi´ I have been using S5timer for the last decade, but every time I have to change the timers from a HMI Panel the problems start, and as I can...
3,484
Heya im doing a small program in gx iec developer 7 and havnt really programmed in years so some help with this would be nice im programming an...
5,475
Hello, I want to create a FC function that uses SCL code that checks deviation of a controllers actual measured value from its setpoint and then...
7,116