I have OB35 created. I inserted Cont_c in rung, addressing it to DB1.
Info:
My A/I address starts at 448 and ends at 463. I set channel 1 to 2dmu current (2 wire transmitter 4-20 mA)and deactivated the other 3 channels.
My A/O address starts at 464 and ends at 471. I set channel 1 to I (current) 4-20 mA and deactivated other 3 channels.
Questions:
#1 - Where do I enter my analog Input and output addresses?
Is it in DB1 under address? PV_PER indicates 14.0 (under address) set for word W#16#0.
LMN_PER indicates 76.0 (under address) set for word W#16#0.
#2 - If I were to create other DB's, would I use these addresses In DB1 for A/I and A/O addresses?
#3 - Can I use OB1 to do the scaling and can I call A/I info or DB info after it has been scaled from DB1?