Safety Circuit Issue
Update:
New contactors ordered for the 4th time to fix the issue.
Machine manufacturer working on a safety compliant retrofit for this whole circuit.
…and also although it was not relevant to the issue, some may be wondering what is purpose of these contactors anyway, as that one single drawing did not tell the whole story?
Update:
New contactors ordered for the 4th time to fix the issue.
Machine manufacturer working on a safety compliant retrofit for this whole circuit.
…and also although it was not relevant to the issue, some may be wondering what is purpose of these contactors anyway, as that one single drawing did not tell the whole story?
- Series NO contacts provided 24VDC to a DIGIN card to indicate all ok with the safety relay and the contactors
- Series NO contacts provided 24VDC path from a DIGOUT card to energize a solenoid permitting machine movement, and required of course as software alone must never be regarded as a safety device
- Two contactors required to prevent a weld-in condition on a single contactor and allowing a false I/O