Scaling Using CX-Programmer
mizuma
Sep 2011
Putrajaya
I am new with Omron PLC. I am currently having problem with SCL block function.
The SCL block function takes input from analog water level sensor (4-20mA).
And using First Parameter Word (I do not know what this mean??) from DM310. How ever DM310 is found to be zero in value thus the result is also zero.
I uploaded the program source code from another PLC and currently trying to download it to the new PLC. The old PLC shows some value for the DM310.
Hope anyone can explain to me what is First Parameter Word and where to set the DM310 value.
- Im using CPU CQM1-H and analog slot ADO41
Thanks in advance,
mizuma
DMXXX is a word or Channel Number. This us a variable you choose
The range is from DM0 upwards
with the Omron Analogue Card you need to note that the input range is
0 ~ 20 mA
As a result you need to insert a value offset for the 4 mA start
the other values are the Minimum 0 scale and the Maximum (100 or whatever) value
the Value you refer to DM310 can be set by the Memory menu on the left
or programmed by a first pass pulse then a move statment
remember to use HEX values
The Instruction Reference under the Help Menu gives you the basics. For more information refer to the Instruction Reference for your Model of PLC, and your Analog Input Card. To see the values of the D/DM Registers, and possibly change them, use the Watch Window in CX-Programmer.
For more information on Scaling in general, see Ron Beauforts excellent write up here.
http://www.ronbeaufort.com/sample_lessons.htm
Links to Scaling Articles.
http://www.ronbeaufort.com/y=mx+b_part1.pdf
http://www.ronbeaufort.com/y=mx+b_part2.pdf
Stu....
hi Stu,
the AB SCP command is very similar to the Omron scale command.
But the analogue card still works from 0 to 20 mA not 4 to 20 mA
so the AB help can be misleading.
Hi Ian:
He is talking about an Omron PLC, which is also what I was referring to. I don't believe I said anything about AB.
Stu....
In CX-P, double click on the SCL command, select detail, select instruction help and the help file will explain how to set up SCL.
It is pretty basic.
I'm having a brain-glitch in trying to display the liquid contents of a silo in kg. There is a 0-1 bar sensor at the base of the silo. The silo...
2,731
Hello, I am a beginner in PLC Programming and FBD language. I faced problem in trying to scale a Analog Input (Temperature Sensor) instruction...
2,882
Hey guys I'm kinda struggling with gx developer and could do with a bit of guidance essentially I have a register (say d10) which is being...
5,556
Can someone explain if there is a way to scale with an offset using the C400 component? (2711C-T4T) In the regular Panelview Standard the...
4,354
Hello I need some help. I am using 1769-IF8 analog input module to measure silo capacity. I have configured my module for engineering units...
24
7,303