So we have a panel. It has 1492-h6 fuse holders in the branch circuits. Will my panel have a max SCCR of 10KA?
10KA is the default SCCR value given to a fuse holder according to UL508A.
The components in the feeder branch all have components rated over 100KA.
Please advise.
10KA is the default SCCR value given to a fuse holder according to UL508A.
The components in the feeder branch all have components rated over 100KA.