Series 90-30 Modbus Communications
csnte14
Dec 2009
Texas
I have a Series 90-30 PLC with a CPU364. Is it possible to configure the RS232 or the 10BaseT port on the cpu as a Modbus RTU Slave? Also, what is the RS232 port labeled 'Station Manager' used for?
Clint
The RS232 "Station Manager" port on the CPU364 is for firmware upgrades. It is not user-configurable. None of the 90-30 CPU models with ethernet have a configurable serial port. If you need both ethernet and Modbus slave capabilities you'll need another module. As diat150 mentioned, you can add a CMM311 module which will give you two ports, either of which can be configured as a Modbus slave. If you're not using the ethernet port, you could replace the (obsolete) CPU364 with a CPU363 which has two configurable serial ports.
You do not need to configure it, just have your master device send it a recognized request and it will reply. If you have problems, make sure that your CPU has the latest firmware, which can be downloaded at the web site also. According to KB5915 it supports Modbus-TCP/IP slave protocol. http://support.gefanuc.com/support/index?page=kbchannel&id=S:KB5915&actp=search Go to the GE web site and get GFK-1541, it will answer your questions about using it. http://support.gefanuc.com/support/...aging/DOCUMENT/0/DO213/en_US/1.0/gfk1541b.pdf
That's right. And you can use EGD.
Hi, I've got a ML 1200 C series with only 1 port and would like to connect to our DCS via Modbus. Since there's only one port, I've decided to...
1,477
Hi Can someone show me an example program of how to set up Modbus using the inbuilt function on the Q03UDVCPU? The manual isn't too clear. I'll...
1,329
Hi I'm wanting to basically get data from a Siemens S7-1200 PLC and write it in to my D registers on my Q series PLC. If I went for profinet...
2,278
Hello people!, I finally was able to get the job done with modbus in my AB ML 1400, now my question is, I´m receiving correctly the information...
1,853
Hi there folks!, I really want some support regarding a damn modbus connection trough channel 1 TCP modbus in my micrologix 1400 b series, I did...
1,945