Set bits and Toggle switches
Greg7683
Jun 2018
Plainfield IN
355
I wrote a program for our Weintek HMI to connect to our Mitsubishi PLC I used two toggle switches for the start buttons but couldn't get the HMI to connect all parameters were set the same. So I switched them to set bits with the same addresses and it connected why wouldn't the toggles connect.
And with macros I don't get it I think I may need to write some macros for a couple of screens but I never wrote a macro before.
I suspect that the problem is probably in the device driver that EZwarePlus loads for your PLC. There have occasionally been similar problems with the Omron drivers.
Why do you think you need to use macros? What do you need to do?
Macros are just scripts that you can run a variety of ways.
Here is an example of one of mine. This is for reading data from an energy meter using Modbus, and then manipulating the data using some functions I wrote. It then puts the resulting data into registers on the HMI to be displayed on screen. I did it this way so the data is calculated in the background and not done when the relevant screen is loaded which slowed down the display of data.
Code:
[COLOR=Red]// Read all data from meter
// Some requires conversion
// Some is used for calcs
macro_command main()
int v, a, em111_s, mcb
float curr, volt, hz, temp_a, temp_v, temp_f
short check, f, status
bool em111_ok, em111_vonly
mcb = 32
// Get Data to do compare for lamp status
GetData(v, "GavazziMeters", "UPSO1L-N", 1)
GetData(a, "GavazziMeters", "UPSO1LC", 1)
GetData(f, "GavazziMeters", "UPSO1FREQ", 1)
GetData(check, "GavazziMeters", 3x, 4#8192, 1)
// Make integer values into floats
temp_v = v
temp_a = a
temp_f = f
// Do comparison for lamp status with function call
em111_s = em111_stat(v,a,mcb)
status = em111_s
em111_ok = em111_on(check)
// Divide data with function call to get
// real value
volt = l_volt(temp_v)
curr = ph_curr(temp_a)
hz = freq(temp_f)
// If voltage but no current make indicator flash
if status == 4 then
    em111_vonly = true
else
    em111_vonly = false
end if
// Set Data in Word for Word lamp
SetData(status,"Local HMI", LW, 303, 1)
SetData(em111_ok, "Local HMI", LB, 103, 1)
SetData(volt,"Local HMI",LW,60,1)
SetData(curr,"Local HMI",LW,62,1)
SetData(hz,"Local HMI", LW, 64, 1)
SetData(em111_vonly,"Local HMI", LB, 203, 1)
end macro_command[/COLOR]
I dont know thats why I am asking on one of our screens in a fuji hmi it has an M on it that looks like the M on the macro button but when I click on it it don't show any thing like that just some $u in the options
Maybe it errors from Weintek Easybuilder Software version please check that software version is lastest.
I have a graphic that has 2 buttons for Automatic and Manual, each with pushbutton animations associated with them to toggle a bit in the PLC, one...
2,520
Hi, I have this code: LAR1 P##structy L 0 T LW [AR1,P#0.0] which resets all the bits in this struct called structy...
642
In a Rx3i what would be the most efficient way to count the number of bits set in a word variable? The naive approach is to simply shift the bits...
1,174
I was always taught to make my software easy to understand and fault find on by anyone reading it. Good practice right? Now I know set and reset...
18
4,729
Using GE RX3i PLC with Machine Edition SW... I have a decimal %R number (value is "1150") that I want to write to a set of 16 %I bits to set 1 and...
18
4,776