I had done a SEW Movidrive Compact project about 2 years ago,and I am going to have a crew install a similar application next week. I have a 4-20 mA signal coming from a PLC telling the drive what speed to go ,on AI 1 Operation Mode
N-Max,4-20 mA Parameter 112. My question is:
What is the best way and easiest way ,to just simply type
in the drive what speed to go, with no external speed reference. I would like for it go 90% all the time. We are
using the same type drive. SEW Movidrive Compact

Thanks,
 
Set N-MIN to 90%, then when you enable the drive your speed is 90%...

I have done it before on some older Movidyne's (not sure of the spelling anymore)
 
Look here http://www.sew-eurodrive.com/download/pdf/11535016.pdf

Starting at page 68,

You will have to disable the current input, do this by par 100 (you will need FIXed)and 11x (it will over-ride the manual setting)

You can have a few different SP's, it looks like 6 look at 160 and 170

301 is you min speed setting

As I said I have never used on of the Movidrives.. but its all there...
 
Use a fixed voltage

The easiest way is to use a pot (5 - 10k, I guess)- and use the analogue input. By that it will be easily adjustable.

:unsure:
 

Similar Topics

Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
32
Views
901
SELECTED NEW FILE SELECTED PROCESSOR TYPE SELECTED I/O CONFIGURATIONS IM UNABLE TO CONFIGURE MY I/O’S. I HAVE A PAPER COPY OF A PROGRAM AND I...
Replies
0
Views
91
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
Replies
9
Views
247
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
93
Hello. I am trying to use a Prosoft AN-X4 to improve the communications for a new panelview plus 7. This is going from a SLC-500 through DH+ to a...
Replies
9
Views
301
Back
Top Bottom