Siemens 319 3PN/DP
randy
Supporting Member
Apr 2002
158
I'm trying to setup the Ethernet port on a new 319 3-PN/DP.
I have the PG/PC Interface setup on "Ethernet Connection (2) I219-LM TCPIP Auto.1. I also have in the properties IE-PG Access Tab "Assign IP addresses unique to project" selected.*
Again just using the Siemens PG unit I can ping the PLC,* compare blocks, and go online with the program. If I select in the IE-PG Access Tab "Do not assign IP addresses automatically" I lose all communication.
Using my standard laptop I cannot ping the PLC. The PLC is an update from a 315 2-DP to a 319 3-PN/DP.
-Randy
-Randy
You didn't specifically include a question, but I assume you'd like an explanation, and help connecting with your standard laptop.
If I recall, "Assign IP addresses unique to project" is used to give your laptop an extra IP address in the correct subnet, if your PC's IP settings wouldn't allow for communication with the PLC.
questions:
1) What IP addresses are assigned to each device (Laptop 1, laptop 2, PLC)
2) Are you connecting directly, or via switches?
3) I'm assuming the PG has TIA Portal. Does your standard laptop have any version of Step 7 on it, or are you only looking for pinging?
I apologize for the structure of the question.
PLC = IP 17.16.20.2 Subnet Mask: 255.255.255.224
Laptop Siemens PG = IP 17.16.20.100 Subnet Mask: 255.255.255.224
Standard Laptop = IP 17.16.20.200 Subnet Mask: 255.255.255.224
Yes the PG has TIA, but I'm using Manager Classic 5.6
No the Standard Laptop does not have any Siemens software.
-Randy
Also when I use the Edit Ethernet node it see the MAC address and I assign a IP and the subnet mask all goes well.
I have not had a problem assigning a IP address
All IPs. If you have subnet 255.255.255.224, you have limited IP range to 30 devices, all devices needs to be on that range.
You can check http://www.subnet-calculator.com/
Leave PLC to IP .2, change laptops somewhere between 1.31 (something like 11 and 12).
Then check with ping command, it should work if there is no firewall softwares.
I've been working for a customer with Siemens Step 7 (classic) PLC automation, using a Siemens Field Service Laptop, and V5.6 of Simatic Manager...
3,036
Hi guys. I been searching and reading a lot about CP341 and other external communications cards on S7-300 series CPU. but I'm still confused...
2,587
I have never installed a brand new CPU before. But, I need to take an existing project from a CPU315 and put it in a CPU319 because we are...
3,119
Hi All I am putting together a largish project at present. The client has requested two off Profibus networks and two off ethernet networks...
2,349
Ok, I want to download my S7 program into my CPU 319-3PN/DP. The problem is I can't even get my PC to talk to the PLC. My ethernet cable is...
2,884