Siemens building automation instruments ( 4 wire ) power supply - plz help

aliabideen

Member
Join Date
Jul 2006
Location
U A E
Posts
1
Dear sir.

We are in the engineering stage of our project..I want to submit material submital to client..

In that complaince statement as per our specification ,all instruments to be loop power from BMS ( siemens DESIGO )..but they are not complying with this..their instruments are 4 wire..

From where all the instrunments will get power?? where is the location of power supply ?? how these impacts to my comp ?

Eg of instruments ( SIEMENS QBE2002-P10 WATER PRESSURE SENSOR , QAE2120.010 IMMERSION TEMP.SENSOR).

the module details are:

1)TXM1.8X ( 4-20 MA AI MODULE) 2)TXM1.16D ( DI INPUT),,
3)TXM1.6R ( DO OUTPUT) 4)TXS1.12F10 (POWER EXT MODULE)

PLEASE I VERY KIND THOSE WHO REPLY..

Thanx

Ali
 

Similar Topics

Hi, We have a Siemens PXC12 PLC controlling our concrete curing ovens. Unfortunately we don't have any way of looking into the program. We have...
Replies
1
Views
1,811
Hey, I'm building a scada program to test PLC programs. Therefor I need to read and write registers, in- and outputs, timers etc. For siemens...
Replies
2
Views
3,614
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
11
Views
273
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
161
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
311
Back
Top Bottom