Siemens cm1241 modbus rtu
Rahul3005
Dec 2017
Mumbai
34
Dear Members ,
I am using a S7-1200 with a communication module CM-1241 , I want to read / write data from few MODBUS devices like PH meter , Density meter etc.
For every MODBUS devices , i have given a unique a node address , and same communication parameters like (baud , stop bit , parity).
I have did the connection as mentioned above in the photo , i have daisychained all modbus devices , I am getting + and -ve cable on my panel.
I have connected +ve to PIN 3 and -ve to PIN 8 and GND to PIN 5 (optional).
Apart from this connection , is there anything more which i need to connect , i heard we have to use terminal resistors in some cases , is using terminal resistors necessary ? also please can u please give me details of communication configuration which i have to do in s7-1200 PLC ?
Thanks and Regards,
Rahul P
For RS485 there is to the best of my knowledge always termination resistors.
You may omit the termination resistors, and it may work, especially at lower baudrates, but the resistance to noise is degraded.
Why even consider it ?
Thanks for the reply , can u share me the photo of how to connect termination resistors and is my connection correct ?
I believe wiring information is in the S7-1200 manual
The resistor values vary quite a bit depending on the manual/example you read. I use 12Ohm on V20 and they work fine but I've read 220Ohm and 330Ohm in two different Siemens manuals. It also states that those recommendations are for cable length longer than 50 meter, I terminate them anyway.
I would go with this link (also see attached image), it shows required resistors to bias and terminate D-Sub.
Read1 ( this is from my Mega, couldn't find the file on the net)
Read2
Been a while since I posted here but I need some help with an S7-1200 and the CM1241 module. I am sending commands to a weigh scale to get the...
2,389
Hey Guys, I hope all is well; quick Question, Background: We have a Siemens OEM Vendor package we were trying to communicate to, and the...
1,610
Hello to all, I'm just starting with using CodeSys. Immediately, I have noticed that Codesys doesn't use data blocks like for example S7 does...
85
104
326
