Siemens ET200 I/O

Banker

Member
Join Date
Dec 2005
Location
aarslev
Posts
82
Hi I have a task to change a controlsystem on a plant. The existing PLC is a Siemens IM 151-8 with a profibus mastercard 6ES7-138-4HA00.
My plan is to skip the CPU and change the profibus mastercard to a slave card and keep the ET200 I/O .Is it possible and if yes what card. ? IM151 ?
 
FYI the ET200S system has just been classified as "Product Phase-Out" by Siemens.

You can replace the IM151-8 CPU with a PROFINET Slave IM:

6ES7151-3BA23-0AB0

The IMs are classed as mature product, but here is the Profibus part#:

6ES7151-1AA06-0AB0

But as for the "Profibus mastercard", there is no replacement. You would have to join what ever Profibus slaves that are there to your new Profibus master - whatever that is.

Can you explain in more detail what you're trying to accomplish? Are you going to use a new S7-1200 or S7-1500 PLC to replace the IM151-8?
 
Hi I have a task to change a controlsystem on a plant. The existing PLC is a Siemens IM 151-8 with a profibus mastercard 6ES7-138-4HA00.
My plan is to skip the CPU and change the profibus mastercard to a slave card and keep the ET200 I/O .Is it possible and if yes what card. ? IM151 ?


if you want to turn the PLC's local IO into a "dumb" IO rack, yes, it's possible. It wouldn't support special cards like the profibus card, but normal IO works fine. There are a few different IMs depending on the functions you need (how fast it updates, is there safety, etc).


That said, ET200S is on the way out, as the other poster said. It is only available as spare parts these days. You might need to ebay it.
 

Similar Topics

Need to create some Logging on a PC from my Siemens ET200SP PLC. Running TIA Portal Ver 14 SP1 Anyone any experience of how to go about this...
Replies
7
Views
2,736
Hello, We have a customer with obsolete S5 Profibus hardware who needs to re-program the Profibus network but does not have the tools necessary...
Replies
3
Views
5,424
Hi all Anybody have an idea , how we configure ET200S hardware.
Replies
8
Views
5,685
V
SIEMENS ET200 NETWORK PROFIBUS, WHEN CHANGE THE MODULE I/O`S NEED POWER OF THE SYSTEM OR CAN CHANGE ON LINE
Replies
4
Views
4,009
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
210
Back
Top Bottom