I have a problem with an FM354 Servo module. There Diag light is on as well as the SF light. I can see the module in Accessible nodes but when I try to go online with the configuration tool, it can’t connect. I’m also not able to download to the FM354.
I then tried it on another system that was fully working and I wasn’t able to go online to the FM354 in that either
My question now is, should I be able to go on line to the servo module? If so, what does anyone have any idea what would prevent me doing so given that I can connect to the PLC and download a program to it?
 
I do and I'm running it in XP.
From the hardware config I can click parameters and the software will open in offline mode
 
In case anyone else comes accross this issue this was from Siemens Support:

"We made the experience that the online connection to FM354 does not work with all adapters, especially non-Siemens adapters have problems establishing a connection to the FM354. Also going online to the FM while PLC is in RUN does in most cases not really work. So the best advice is to try with the PLC being set to STOP."
 
The problem with the servo turned out to be the Flash Memory module in the CPU, must have some how been dragging the 5v down, nothing else on the rack was affected, I've never seen anything like that happen before
 

Similar Topics

Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
4
Views
69
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
Replies
5
Views
107
Hello to all, I'm just starting with using CodeSys. Immediately, I have noticed that Codesys doesn't use data blocks like for example S7 does...
Replies
11
Views
164
Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
111
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
330
Back
Top Bottom