Siemens PLC and GE drives

krome

Member
Join Date
Jan 2009
Location
michigan
Posts
31
I have a Siemens S7-300 CPU going to used profibus to talk to a GE drive AF-650. I was wondering if someone could help me out to understand the PPO type? Which one should i use. I want to tell the drive to turn on and off and send speed ref to the drive. as well as get if the drive is running what speed is going, voltage or current, any fault on the drive.

Thanks for your help
 
I poked around on the GE website. Are these really brand
Labeled from Danfoss?

Anyway, I didn't find a layout of the control word.
Can you also post the gsd file?
 
Yes it an AF-600 FB or a AF-650 GP there fan and pump drives. attach is the gsd file as well as the control word
 
Its looks simple enough. Use PPO3 for starters.
If you keep it simple and
use a couple of move commands
with a conditional 047C and a 043C to PQW264- does the drive enable?
Also with a value to PQW266 for speed reference

I THINK Im seeing the control word bit pattern correct- Im not sure
about START verses ENABLE

Anyway- try it

What happens?
What parameters in the drive "turn on" profibus communications?
 
13 years later and people are still using the GE 650 drives...

working on a PLC upgrade from GE to Rockwell. can someone please post the GSD file for the GE AF-650 drive? I cannot find it on the web anywhere.
 

Similar Topics

I have a Siemens S7-300 CPU going to used profibus to talk to a GE drive AF-650. I was wondering if someone could help me out to understand the...
Replies
0
Views
1,641
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
4
Views
52
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
Replies
5
Views
171
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
335
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
154
Back
Top Bottom