Hi
I have a problem with a new installation.
PLC is node 2, HMI 1 is node 3 and HMI 2 is noode 4
If I view accesible nodes I see everything, and can prove the hmi node address by powering down a node
If I download to node 3, node 3 is overwritten. If I download to node 4, node 3 gets overwritten.
Weird behaviour, and yes i checked the nodes profibus address under transer..advanced..profibus
I am using WinCC Flex 2008 SP3
Also what is the thinking behind 'only master on the bus'
Cheers
Are you POSITIVE when you press the transfer button
that you are down loading to 4 (your station address is not set to 3)
see pic
I know, I really read your post- just checking :)
that is odd
Yes I am.
Although I have made the mistake before :)
Maybe I need to apply > exit transfer, and reopen transfer and check it has accepted the node change.
I tried an ethernet transfer and the panel would not accept it but i think my cat5 lead is suspect
Hi...Yes
I the project I have 2 CPU's, 4 HMIs and 2 servos on profibus
Each CPU has its own Profibus network (Profi1 and Profi2) and each network is a PLC,2 HMIs and a servo
Profi 2 works 100% ok
Difference between them is that all profibus address are unique because customer wants to integrate the 2 systems later but we we designing it as 2 seperate systems so originally I had the profi networks identical
PLC (2),,HMI(3),,HMI(4)..SERVO(5) <-- original profi 1 & 2 now just Profi1
PLC(6)..HMI(7)..HMI(8)..SERVO(9) <--- new profi 2
Also ... My WinCC always shows GERMAN text on startup in the "WinCC is starting" dialod from within Simatic manager but I can live with that but I am wondering about corruption somewhere
Hi
Further to this I went to work today and found my USB Profibus adaptor would not work AT ALL with anything so I suspect my issues were done to that. I will have a new shiney one tommorow to retry
If you put 4 HMIs on one profibus network it will slow that network significantly because profibus uses token passing between masters and a master con only communicate with its slaves when in possesion of the token. So if you have 4 HMIs and 2 CPUs on one network there will be 6 masters!
My advice would be: 1) use Ethernet instead 2) put the HMIs on a separate network.
Good luck with your anomally.
Nick
Hi I have 2 independant networks of 1 plc and 2 hmi each plus a servo drive.
The customer wants to integrate and have their own controls people so i will let them decide on that themselves :)
They asked for Profibus specifically
+1 what Manglemender said.
Oh, in addition to slowing down the system, it also becomes much more inflexible. Think about that with many CPUs and HMIS in the same system, it is quite plausible that you will need to reconfigure, replace, shutdown for maintenance etc., which will affect the system if it is running 24/7. Sometimes you cannot get to reconfigure it because if this. Another reason for separating the higher level "bus" with the lower level fieldbus. Also do not physically wire individual logical fieldbusses together, thats what DP/DP couplers are for.
Customers sometimes are less qualified incertain technical aspects than they think themselves. Be sure to officially explain to them the consequences if they ho ahead with their own ideas. Customers also sometimes have strange ideas about who is responsible when it goes wrong. Since they explained how they want to do it, and if you do not protest, then you become part responsible. Just saying.
+1 What Jesper said.
In my experience, custometrs often need to be "Educated" and they WILL call you when it doesn't work.
My other favourite is "we want you to use these blocks that we've written" which are, almost invariably, appalingly badly written. The phrase "why have a dog and bark yourself?" comes to mind.
Nick
Oh another good one.
If everything is hooked together in one big Profibus system, one error can bring everything down.
And yet another one.
If the big system is down, with everything connected together it becomes MUCH MUCH harder to pinpoint the error.
Big profibus systems --> Set aside the expense for and buy a Profibus analyser for the day when you are going to need it.
Hi All
We have already expressed concerns officially and had to do design and document changes to get to Profibus
Cheers for your points. PS It is all working fine with the new adaptor
It still makes no sense that you download to hmi address 4 and hmi 3 recieves the configuration
Anyway- Im glad its working
Hey All, I am trying to get a Phoenix Contact ILC171 to communicate with a Siemens CU320 via a profibus module (IB IL PB MA-Pac). I currently...
5,928
I'm just trying to figure out the right method of adding a DO card to an existing rack. It's not the *next* open slot, but I have to move the AO...
567
Kindly, we are trying to go online on an S7-300 plc, with profibus communication, using a CP5711 adapter. But when we open the Ladder and press...
793
I'm trying to figure out how to read the actual speed reference value from the move blocks, writing to a DB that is being sent to the VFD. For...
2,649
I have a piece of equipment with control split between two PLCs. A quantum 434, and a Siemens S7-300, communicating via profibus. I have a prosoft...
5,338