The S7-1200 CPU operates ten RTMs (Run-Time hour Meters). The NR input parameter to the RTM instruction determines which of those ten that instruction uses. Since the value of NR is the same, i.e. 0, on all of the RTM instructions in the program, the CPU uses the same, i.e. only one, run-time hour meter for all of those instructions.
So when you wrote "I have more than one RTM in my program," you should have written "I have only one RTM in my program" instead.