i have been looking at a siemens s212 datasheet and dont understand what per single point, per 2 adjacent points and all points total means. the sub title says maximum load current, so i presume its something to do with that. could someone explain to me what it means, in simple terms as i am a begineer. thanx
 
They're talking about how much load you can put on the output module. Outputs usually share a 'common' terminal, so there is a maximum rating on that terminal. That's your 'all points total' number. The 'single point' number is the maximum load each individual output can handle. All individual outputs at their maximum rated output is often more than the single common can handle.

For example, let's say you have an output module with 4 outputs per common that's rated 1A 'single point', and 3A 'all points total'. Even though you're allowed 1A per point, if you actually USE 1A at each point, you're pulling 4A through the common terminal. That exceeds the 3A 'all points total'.

I'm not sure what the 'adjacent points' is referring to. What specific module are you using?

beerchug

-Eric
 

Similar Topics

Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
91
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
322
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
168
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
319
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
132
Back
Top Bottom