In Simatic Manager Hardware Configuration, Profibus shows up its stations in a graphical view.

Is there a way to display the AS-i nodes in a graphical way?
Is there an add-in software that will?

I've dealt with S5 but S7 is further complicated. Why change S5's PB's to S7's FC's? Bloody awkward Germans; good engineers though.
 
Hello silva.foxx;

In the Hardware configurator of Step7, AS-i nodes are represented only as a collection of bytes; you have no way of representing them either graphically or symbolically.
Of course, in your HMI package you can animate a graphic presentation ofyour nodes. This is what we did in all our AS-i connected projects.
Hope this helps,
Daniel Chartier
 

Similar Topics

I have never had the pleasure of working with a "Thermistor" until now and have a question. The Thermistor is a 10KOhm 4-20mA 2-wire device and I...
Replies
3
Views
73
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
9
Views
176
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
12
Views
432
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
123
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
174
Back
Top Bottom