siemens s7 symbolic field list
adamplc
Dec 2009
usa
92
I have a problem and cannot find a good solution for a list of part #'s on a HMI. I have around 30 int #'s thats just say 0-29 from a symbolic field that the operator can change to various different products. if the operator changes the list to something else say was on 0 and change it to 20 I wish to know it has been changed to trigger the machine change.
What is the best way to see if the list has been changed.
Thanks for any help
As I see your question, you want to trigger a bit in the PLC when the operator changes the input field on the HMI.
PLC pseudocode:
Code:
IF HMI_selection_input = HMI_selection_memory THEN
  HMI_selection_was_changed := FALSE
ELSE
  HMI_selection_was_changed := TRUE
END_IF
HMI_selection_memory := HMI_selection_input
IF HMI_selection_was_changed THEN
// do the activity
Have a copy of the list. Compare the two lists, if they are different, flag a machine change. Update the copy.
Thou both solutions are great they seem to exceed my abilities as i'm a little noob with siemens.
L D[AR2,#P0.0] how do you update the list after the compare?
In the HMI software you can set the event of the HMI tag.
Set it to "set bit" and your done.
Code:
       L #HMI_value1
       L #HMI_copy_value_1
       <>I
       JC Diff
       JU OK
Diff: // Perform whatever action you want to happen after a change here
OK:    L #HMI_value1
       T #HMI_copy_value_1
What about something like that??
(Not tested but looks like it should work...)
You'd need one for each of the thirty INT's but you could set up a function that you pass in the value and the 'output' and then just cycle through the thirty INT's...
I was also not wanting to set events through the hmi. I already got to the point of uptown's solution but it is just so cumbersome lots of compares not sure if the pointer is a good way or not as I didn't fully understand them is this an option?
Yes. Write a function with 3 input parameters; pointer to table, pointer to copy, number of entries to scan. Return value is a bool which will be true of the table has changed.
Not sure if I got it right, is it 1 Symbolic field with 30 entries or 30 different Symbolic fields with each 30 entries?
In stead of Range (...-...) use Btinumber (0-31) (warning: this limits future selections to 32max)
Said Text list is linked to Symbolic IO-field which is linked to Doubleword tag.
Each bit in this doubleword is a 'product choice'.
Positive edge detected on bit will start corresponding changeover.
Or you could just do:
Code:
      L #HMI_copy_value_1
      L #HMI_value1
      <>I
      JC Diff
      JU OK
Diff: NOP 0
      JL err    // If selection falls outside max programmed selections
      JU PR00   // Product 00 (Symbolic selection  = 0)
      JU PR01   // Product 01 (Symbolic selection  = 1)
      JU PR29   // Product 29 (Symbolic selection  = 29)
PR00: NOP 0
// Set trigger bit for changeover to product 0
// And some other stuff if needed
      JU OK
PR01: NOP 0
// Set trigger bit for changegover to product 1
      JU OK
PR29: NOP 0
// Set trigger bit for changegover to product 29
     JU OK
OK:  L #HMI_value1
     T #HMI_copy_value_1
The moment a change in value is detected, it will jump to the relevant spot in the list and trigger anything you want to do.
from here on you have several choices, either do this for only one scan when it changes, or keep going through the code until the changeover is completed.
For the latter, you will have to add a jump over the OK label.
Note: The example one is limited to 256 selections and doesn't really accept gaps in the number of JU. (read the F1 for more information)
As I understood it though, you need to know which entry has changed and not just that any entry has changed?? Is this correct??
I just need to know it has changed I like what L D[AR2,0.0] has done many thanks, but in order for me to understand when pointing to w 0.0 i am pointing at the db # correct?
When pointing at the D 2.0 within the AR am I pointing at the area?
I feel a burger moment coming on!
Hello, I am new to Siemens programming. I have been an Allen-Bradley guy for years (20+). I am struggling to understand some of the language...
6,010
21
139
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
170